Before you install a Lenovo Storage V seriessystem, your physical environment must meet certain requirements. This includes verifying that adequate space is available and that requirements for power and environmental conditions are met.
This information pertains to Lenovo Storage V7000 Gen1 environmental requirements. For Lenovo Storage V7000 Gen2 requirements, search for the words power cooling at the following website:
http://support.lenovo.com/us/en/products/servers/lenovo-storage
Use the following general safety information for all rack-mounted devices:
Ensure that your environment meets the following power requirements.
To aid in power and cooling requirements planning, Table 1 lists the rating of each power supply unit (PSU) by enclosure.
The power used by the system depends on a variety of factors, including the number of enclosures and drives in the system and the ambient temperature.
Model and type | PSU | Input power requirements | Maximum input current | Maximum power output | Caloric value (BTU/hr) |
---|---|---|---|---|---|
2076-112 Control Enclosure with 12 3.5-inch drive slots | 764 W (2) | 100V to 240V single phase ac At a frequency of 50 Hz or 60 Hz |
10A for 100V 6A for 240V |
764 W | 2607 |
2076-124 Control Enclosure with 24 2.5-inch drive slots | |||||
2076-212 Expansion Enclosure with 12 3.5-inch drive slots | 580 W (2) | 100V to 240V single phase ac At a frequency of 50 Hz or 60 Hz |
8A for 100V 6A for 240V |
580 W | 1980 |
2076-224 Expansion Enclosure with 24 2.5-inch drive slots | |||||
2076-312 Control Enclosure with 12 3.5-inch drive slots and 10 Gbps Ethernet adapter | 764 W (2) | 100V to 240V single phase ac At a frequency of 50 Hz or 60 Hz |
10A for 100V 6A for 240V |
764 W | 2607 |
2076-324 Control Enclosure with 24 2.5-inch drive slots and 10 Gbps Ethernet adapter | |||||
2076-524 Control Enclosure with 24 2.5-inch solid state drives, 2 host adapters, 2 compression accelerators | 1200 W (2) | 100V to 240V single phase ac At a frequency of 50 Hz or 60Hz |
12A for 100V 7A for 240V |
452 W | 1542 |
2076-524 Control Enclosure with 24, 10k SAS Drives, 2 host adapters, 2 compression accelerators | 1200 W (2) | 100V to 240V single phase ac At a frequency of 50 Hz or 60Hz |
12A for 100V 7A for 240V |
430 W | 1467 |
2076-524 Control Enclosure with 24, 15k SAS Drives, 2 host adapters, 2 compression accelerators | 1200 W (2) | 100V to 240V single phase ac At a frequency of 50 Hz or 60Hz |
12A for 100V 7A for 240V |
471 W | 1607 |
Model and type | Configuration | Total power consumption | Caloric value (BTU/hr) |
---|---|---|---|
2076-124 | 1 enclosure with 24 10K RPM SAS Drives | 410 W | 1400 |
2076-224 | 1 enclosure with 24 10K RPM SAS Drives | 205 W | 700 |
2076-212 | 1 enclosure with 12 7.2K RPM nearline SAS Drives | 175 W | 600 |
2076-312 | 1 enclosure with 12 7.2K RPM nearline SAS Drives and 10 Gbps Ethernet adapter | 380 W | 1300 |
2076-324 | 1 enclosure with 24 flash drives and 10 Gbps Ethernet adapter | 530 W | 1800 |
2076-324 | 1 enclosure with 24 10K RPM SAS Drives and 10 Gbps Ethernet adapter | 410 W | 1400 |
2076-524 | 1 enclosure with 24 2.5-inch solid state drives, 2 host adapters, 2 compression accelerators | 452 W | 1542 |
2076-524 | 1 enclosure with 24 10K SAS drives, 2 host adapters, 2 compression accelerators | 430 W | 1467 |
2076-524 | 1 enclosure with 24 15K SAS drives, 2 host adapters, 2 compression accelerators | 471 W | 1607 |
2076-24F | 1 enclosure with 24 2.5-inch flash drives | 151 W | - |
2076-24F | 1 enclosure with 24 10K SAS drives | 175 W | - |
2076-24F | 1 enclosure with 24 15K SAS drives | 234 W | - |
2076-24F | 1 enclosure with 12 7.2K nearline SAS drives | 158 W | - |
Each Lenovo Storage V series enclosure contains two PSUs for redundancy. The total power consumption values represent the total power drawn by both PSUs.
Ensure that your environment falls within the ranges shown in Table 3.
Environment | Ambient temperature | Altitude | Relative humidity | Maximum wet bulb temperature |
---|---|---|---|---|
200W operating | 5°C to 40°C (41°F to 104°F) | 0 to 2133 m (0 to 7000 ft) | 8% to 80% noncondensing | 23°C (73°F) |
5°C to 35°C (41°F to 95°F) | 2134 to 3048 m (7001 to 10000 ft) | |||
400W operating | 5°C to 35°C (41°F to 95°F) | 0 to 2133 m (0 to 7000 ft) | 8% to 80% noncondensing | 23°C (73°F) |
5°C to 30°C (41°F to 86°F) | 2134 to 3048 m (7001 to 10000 ft) | |||
Non-operating | 1°C to 50°C (34°F to 122°F) | -305 to 12192m (-1000 to 40000 ft) | 8% to 80% noncondensing | 27°C (80°F) |
Storage | 1°C to 60°C (34°F to 140°F) | 5% to 80% noncondensing | 29°C (84°F) | |
Shipping | -40°C to 60°C (-40°F to 140°F) | 5% to 100% condensing, but not precipitating |
Ensure space is available in a rack, capable of supporting the enclosure based on the data shown in Table 4.
Enclosure | Height | Width | Depth | Maximum weight | |
---|---|---|---|---|---|
Drive ready (without drive modules) | Fully configured (with drive modules) | ||||
2076-112, 2076-212, and 2076-312 Control Enclosures with 12 drive slots | 87.9 mm |
483 mm |
630 mm |
17.1 kg |
27.2 kg |
2076-124, 2076-224, and 2076-324 Control Enclosures with 24 drive slots | 87.9 mm |
483 mm |
630 mm |
17.1 kg |
25.2 kg |
2076-524 Control Enclosures with 24 drive slots | 87 mm |
483 mm |
730 mm |
28.2 kg |
36.5 kg |
2076-12F Expansion Enclosure with 12 drive slots | 87 mm |
483 mm |
556 mm |
16.4 kg |
26.7 kg |
2076-24F Expansion Enclosure with 24 drive slots | 87 mm |
483 mm |
556mm |
16.7 kg |
25.0 kg |
Ensure that these additional space requirements, as shown in Table 5, are available around the enclosures.
Location | Additional space requirements |
Reason |
---|---|---|
Left and right sides | 50 mm (2 in.) |
Cooling air flow |
Back | Minimum: 100 mm (4 in.) |
Cable exit |
Table 6 provides drive specifications for your Lenovo Storage V series system.
Model and type | 3.5-inch drives | 2.5-inch drives |
---|---|---|
2076-112 Control Enclosure with 12 3.5-inch drive slots | 2 TB 3.5" 7.2K RPM Nearline SAS drive | - |
2076-124 Control Enclosure with 24 2.5-inch drive slots | - |
|
2076-212 Expansion Enclosure with 12 3.5-inch drive slots | 2 TB 3.5" 7.2K RPM Nearline SAS drive | - |
2076-224 Expansion Enclosure with 24 2.5-inch drive slots | - |
|
2076-312 Control Enclosure with 12 3.5-inch drive slots and 10 Gbps Ethernet adapter | 2 TB 3.5" 7.2K RPM Nearline SAS drive | - |
2076-324 Control Enclosure with 24 2.5-inch drive slots and 10 Gbps Ethernet adapter | - |
|
2076-524 Control Enclosure with 24 2.5-inch drive slots | - |
|
2076-12F Expansion Enclosure with 12 3.5-inch drive slots | 3.5” 7.2K RPM HDD 2 TB, 3 TB, 4 TB, 6 TB, 8 TB | - |
2076-24F Expansion Enclosure with 24 2.5-inch drive slots | - |
|
The Lenovo Storage V7000 Gen1 models support up to 240 drives in the system with RAID levels 0, 1, 5, 6, and 10. The Lenovo Storage V7000 Gen2 model supports up to 504 drives in the system with RAID levels 0, 1, 5, 6, and 10.
Model and type | Acoustical output per enclosure |
---|---|
2076-112 Control Enclosure with 12 3.5-inch drive slots | Less than 7.4 B LwA -- Operating (40% Average seek rate) @ 23°C ambient |
2076-124 Control Enclosure with 24 2.5-inch drive slots | Less than 7.4 B LwA -- Operating (40% Average seek rate) @ 23°C ambient |
2076-212 Expansion Enclosure with 12 3.5-inch drive slots | Less than 6.3 B LwA -- Operating (40% Average seek rate) @ 23°C ambient |
2076-224 Expansion Enclosure with 24 2.5-inch drive slots | Less than 6.3 B LwA -- Operating (40% Average seek rate) @ 23°C ambient |
2076-312 Control Enclosure with 12 3.5-inch drive slots | Less than 7.7 B LwA -- Operating (40% Average seek rate) @ 23°C ambient |
2076-324 Control Enclosure with 24 2.5-inch drive slots | Less than 7.7 B LwA -- Operating (40% Average seek rate) @ 23°C ambient |
2076-524 Expansion Enclosure with 24 2.5-inch drive slots | Less than 6.5 B LwA -- Operating (40% Average seek rate) @ 23°C ambient |
2076-524 Control Enclosure with 24 2.5-inch drive slots | Less than 6.3 B LwA – Operating (40% Average seek rate) @ 23°C ambient |
The noise emission level stated is the declared (upper limit) sound power level, in decibels, for a random sample of machines. All measurements are made in accordance with ISO 7779 and reported in conformance with ISO 9296.
Table 8 and Table 9 provide the shock and vibration testing results for your Lenovo Storage V series system.
Shock categories | Test level | Performance |
---|---|---|
Operational | 5g 10ms 1/2 Sine | <=25g 10ms |
Non-operational | 30g 10ms 1/2 Sine | <=75g 11ms |
Vibration categories | Test level | Performance |
---|---|---|
Operational | 0.21 grms 5-500Hz Random | Throughput loss <=10% FCAL <= 0.68 grms |
Non-operational | 1.04 grms 2-200Hz Random | <=3.12 grms |
Shipping | 0.3g 2-200Hz Sine | <=5g |
Rotational vibration | Normal operation performance measurements in enclosure with no external vibration. | Throughput loss for all drives of the same type within performance profile. |