Before you install a system, your physical environment must meet certain requirements. This includes verifying that adequate space is available and that requirements for power and environmental conditions are met.
Use the following general safety information for all rack-mounted devices:
To aid in power and cooling requirements planning, Table 1 lists the rating of each power supply unit (PSU) by enclosure. Each enclosure contains two AC PSUs for redundancy. The power rating values represent the total power drawn by both PSUs. The power that is used by the system depends on various factors, including the number of enclosures and drives in the system and the ambient temperature.
Model and type | PSU | Input power requirements | Maximum input current | Maximum power output | Caloric value (BTU/hr) |
---|---|---|---|---|---|
Lenovo Storage V series | AC 800 W | Single phase AC: 100 V to 127 V or 200 V
to 240 V Frequency: 50-60 Hz |
100 V to 127 V 9 A 200 V to 240 V 4.5 A |
800 W | 2730 |
The measurements that are shown in the following tables were obtained in the specific operating environment and under the conditions described. These measurements are presented as an illustration; measurements that are obtained in other operating environments might vary. Conduct your own testing to determine specific measurements for your environment.
Table 2 shows examples of the power ratings of Lenovo Storage V series systems with different drive configurations.
Drive type | Lenovo Storage V3700 V2 | Lenovo Storage V3700 V2 XP | Lenovo Storage V5030 | ||||||
---|---|---|---|---|---|---|---|---|---|
Average | Peak | Idle (Average) | Average | Peak | Idle (Average) | Average | Peak | Idle (Average) | |
24-off Flash | 287 W | 292 W | 245 W | ||||||
24-off 15 K | 366 W | 370 W | 341 W | ||||||
24-off 10 K | 327 W | 327 W | 306 W | ||||||
12-off LFF NL | 252 W | 254 W | 242 W | 292 W | 277 W | ||||
Workload: 70/30 random cache miss; worst of 4 K or 256 K block
size.
|
Table 3 shows examples of the power ratings of Lenovo Storage V series expansion enclosures with different drive configurations.
Drive type | Expansion enclosure | ||
---|---|---|---|
Average | Peak | Idle (Average) | |
24-off 15 K | 234 W | 245 W | 199 W |
24-off SFF NL | 193 W | ||
12-off LFF Flash | 150 W - 180 W | ||
12-off LFF NL | 166 W | 165 W | |
Workload: 70/30 random cache miss; 4 K block size.
|
Environment | Ambient temperature | Altitude | Relative humidity | Maximum dew point |
---|---|---|---|---|
Operating | 10° C to 35° C (50° F to 95° F) | 0 - 3050 m (0 - 10,006 ft) | 20% to 80% non-condensing | 21°C (69° F) |
Non-operating | -10° C to 50° C (14° F to 125° F) | 0 - 3050 m (0 - 10,006 ft) | 8% to 80% non-condensing | 27°C (80° F) |
Storage | 1° C to 60° C (33° F to 140° F) | No limit | 5% to 80% non-condensing | 29°C (84° F) |
Shipping | -40° C to 60° C (-40° F to 140° F) | No limit | 5% to 100% non-condensing | 29°C (84° F) |
Table 5 summarizes the dimension and weight information for the Lenovo Storage V series control and expansion enclosures. Ensure that the rack has enough available space to support each type of enclosure.
Enclosure type | Model | Height | Width | Depth | Maximum weight | |
---|---|---|---|---|---|---|
Drive ready (without drive modules) | Fully configured (with drive modules) | |||||
Control enclosures (12 LFF drive slots) |
|
8.7 cm |
48.3 cm |
55.6 cm |
18.0 kg |
28.3 kg |
Control enclosures (24 SFF drive slots) |
|
8.7 cm |
48.3 cm |
55.6 cm |
19.0 kg |
27.3 kg |
Expansion enclosure (12 LFF drive slots) |
|
8.7 cm |
48.3 cm |
55.6 cm |
16.4 kg |
26.7 kg |
Expansion enclosure (24 SFF drive slots) |
|
8.7 cm |
48.3 cm |
55.6 cm |
16.7 kg |
25.0 kg |
Ensure that additional clearance, as shown in Table 6, is available around each of the control and expansion enclosures.
Location | Space requirement | Reason |
---|---|---|
Left and right sides | 50 mm (2 in.) | Cooling air flow |
Back | Minimum: 100 mm (4 in.) | Cable exit |
Table 7 shows the drive specifications for the control and expansion enclosures of Lenovo Storage V series systems.
Enclosure type | Drive type and storage capacity |
---|---|
Enclosures with 12 drive slots
|
|
Enclosures with 24 drive slots
|
Table 8 provides the acoustical specifications for Lenovo Storage V series systems. The noise emission level that is stated is the declared (upper limit) sound power level, in decibels, for a random sample of enclosures. All measurements are made in accordance with ISO 7779 and reported in conformance with ISO 9296.
Enclosure type | Drive configuration | Acoustical output per enclosure | |
---|---|---|---|
Idling | Operating | ||
Control enclosure | 12 LFF drives | 6.2 bels | 6.1 bels |
24 SFF drives | 6.2 bels | 6.1 bels | |
Expansion enclosure | 12 LFF drives | 6.1 bels | 6.1 bels |
24 SFF drives | 6.2 bels | 6.2 bels |
Table 9 provides the shock testing results for each Lenovo Storage V series system.
Shock categories | Test level | Performance |
---|---|---|
Operational | 5 g 10 ms 1/2 Sine | <=25 g 10 ms |
Non-operational | 30 g 10 ms 1/2 Sine | <=75 g 11 ms |
Table 10 provides the vibration testing results for Lenovo Storage V series systems.
Vibration categories | Test level | Performance |
---|---|---|
Operational | 0.21 grms 5-500 Hz Random | Throughput loss <=10% FCAL <= 0.68 grms |
Non-operational | 1.04 grms 2-200 Hz Random | <=3.12 grms |
Shipping | 0.3 g 2-200 Hz Sine | <=5 g |
Rotational vibration | Normal operation performance measurements in enclosure with no external vibration. | Throughput loss for all drives of the same type within performance profile. |
Table 11 provides the supported depth of the rack for each Lenovo Storage V series system.
Rack | Supported depth |
---|---|
Standard, 19-inch | 69.0 cm to 75.0 cm |