Problem: Storwize V7000 Gen2 SAS cabling not valid

This topic provides information to be aware of if you receive errors that indicate the SAS cabling is not valid.

Check the following items:
  • No more than 10 expansion enclosures can be chained to port 1 (below the control enclosure). The connecting sequence from SAS port 1 of the node canister is called chain 1.
  • No more than 10 expansion enclosures can be chained to port 2 (above the control enclosure). The connecting sequence from SAS port 2 of the node canister is called chain 2.
  • Do not connect a SAS cable between a port on a left canister and a port on a right canister.
  • In any enclosure, the same ports must be used on both canisters.
  • Do not connect a SAS cable between ports in the same enclosure.
  • In each enclosure, where a cable connects from SAS port 1 of the left canister to another enclosure, a cable must also connect from SAS port 1 of the right canister to the other enclosure. Similarly, where a cable connects from SAS port 2 of the left canister to another enclosure, a cable must also connect from SAS port 2 of the right canister to the other enclosure.
  • For cables connected between expansion enclosures, one end is connected to port 1 while the other end is connected to port 2.
  • For cables that are connected between a control enclosure and expansion enclosures, port 1 must be used on the expansion enclosures.
  • The last enclosure in a chain must not have cables in port 2 of the left canister, nor port 2 of the right canister.
  • Ensure that each SAS cable is fully inserted.