1145: The signal connection between a 2145 and its 2145 UPS is failing.

Explanation

The signal connection between a 2145 and its 2145 UPS is failing.

User Response

  1. If other nodes that are using this uninterruptible power supply are reporting this error, exchange the 2145 UPS electronics unit for a new one.
  2. If only this node is reporting the problem, check the signal cable, exchange the FRUs for new FRUs in the sequence shown.
  3. Check the node status:
    • If all nodes show a status of online, mark the error as fixed.
    • If any nodes do not show a status of online, go to the start MAP.
    • If you return to this step, contact your support center to resolve the problem with the uninterruptible power supply.
  4. Go to the repair verification MAP.

Possible Cause, FRUs, or other:

2145-CF8 or 2145-CG8

N/A