Explanation
The 2145 UPS-1U has reported that it has a problem
with the input AC power.
User Response
- Check the input AC power, whether it is missing or out of specification.
Correct if necessary. Otherwise, exchange the FRU for a new FRU.
- Check node status. If all nodes show a status of "online",
mark the error that you have just repaired "fixed". If any nodes
do not show a status of "online", go to start MAP. If you return
to this step, contact your support center to resolve the problem with
the uninterruptible power supply.
- Go to repair verification MAP.
Possible Cause-FRUs or other:
- 2145 UPS-1U input power cable (10%)
- 2145 UPS-1U assembly (10%)
Other:
- The input AC power is missing (40%)
- The input AC power is not in specification (40%)