1093: The internal temperature sensor of the 2145 has reported that the temperature warning threshold has been exceeded. For the 2145-DH8 and 2145-CF8 only, the CPU temperature is too high.

Explanation

The internal temperature sensor of the 2145 has reported that the temperature warning threshold has been exceeded.

User Response

  1. Ensure that the internal airflow of the node has not been obstructed.
  2. Check node status. If all nodes show a status of "online", mark the error that you have just repaired "fixed". If any nodes do not show a status of "online", go to the start MAP. If you return to this step, contact your support center to resolve the problem with the 2145.
  3. Go to repair verification MAP.
For the 2145-DH8 and 2145-CF8 only:
  1. Check for external air flow blockages.
  2. Remove the top of the machine case and check for missing baffles, damaged heatsinks, or internal blockages.
  3. If the problem persists after taking these measures, replace the CPU assembly FRU if 2145-DH8 or 2145-CF8.

Possible Cause-FRUs or other:

2145-CF8 or 2145-CG8
  • Fan module (20%)
  • System board (5%)
  • Canister (5%)

Possible Cause-FRUs or other:

2145-DH8 or 2145-CF8
  • CPU assembly (30%)

Other:

Airflow blockage (70%)