Explanation
The temperature soft or hard shutdown threshold
of the 2072 has been exceeded. The 2072 has automatically powered
off.
User Response
- Ensure that the operating environment meets specifications.
- Ensure that the airflow is not obstructed.
- Ensure that the fans are operational.
- Go to the light path diagnostic MAP and perform the light path
diagnostic procedures.
- Check node status. If all nodes show a status of "online",
mark the error that you have just repaired as "fixed". If any
nodes do not show a status of "online", go to the start MAP.
If you return to this step, contact your support center to resolve
the problem with the 2145.
- Go to the repair verification MAP.
Possible Cause-FRUs or other:
2072 - Node Canister
(100%)
- The FRU that is indicated by the Light path diagnostics (25%)
- System board (5%)
Other:
System environment or airflow blockage (70%)