Explanation
One of the two power supply
units in the node is either missing or has failed.
Note: This error
is reported when a hot-swap power supply is removed from an active
node, so it might be reported when a faulty power supply is removed
for replacement. Both the missing and faulty conditions report this
error code.
User Response
Error code 1096 is reported
when the power supply either cannot be detected or reports an error.
- Ensure that the power supply is seated correctly and that the
power cable is attached correctly to both the node and to the 2145
UPS-1U.
- If the error has not been automatically marked fixed after two
minutes, note the status of the three LEDs on the back of the power
supply.
- If the power supply error LED is off and the AC and DC power LEDs
are both on, this is the normal condition. If the error has not been
automatically fixed after two minutes, replace the system board.
- Follow the action specified for the LED states noted in the table
below.
- If the error has not been automatically fixed after two minutes,
contact support.
- Go to repair verification MAP.
Error,AC:Action
ON,ON or OFF,ON or OFF:The power supply
has a fault. Replace the power supply.
OFF,OFF,OFF:There is
no power detected. Ensure that the power cable is connected at the
node and 2145 UPS-1U. If the AC LED does not light, check the status
of the 2145 UPS-1U to which the power supply is connected. Follow
MAP 5150 2145 UPS-1U if the UPS-1U is showing no power or an error;
otherwise, replace the power cable. If the AC LED still does not light,
replace the power supply.
OFF,OFF,ON:The power supply has a
fault. Replace the power supply.
OFF,ON,OFF:Ensure that the
power supply is installed correctly.
Possible Cause-FRUs or
other:
Failed PSU:
- Power supply (90%)
- Power cable assembly (5%)
- System board (5%)
Missing PSU:
- Power supply (19%)
- System board (1%)
- Other: Power supply not correctly installed (80%)