Explanation
One of the two power supply units in the node is
either missing or has failed.
Note: This error is reported when a hot-swap power supply is removed from an active node, so it
might be reported when a faulty power supply is removed for replacement. Both the missing and faulty
conditions report this error code.
User Response
Error code 1096 is reported when the power supply
either cannot be detected or reports an error.
- Ensure that the power supply is seated correctly and that the power cable is attached correctly
to both the node and to the 2145 UPS-1U.
- If the error has not been automatically marked fixed after two minutes, note the status of the
three LEDs on the back of the power supply.
- If the power supply error LED is off and the AC and DC power LEDs are both on, this is the
normal condition. If the error has not been automatically fixed after two minutes, replace the
system board.
- Follow the action specified for the LED states noted in the table below.
- If the error has not been automatically fixed after two minutes, contact support.
- Go to repair verification MAP.
Error,AC,DC:Action
ON,ON or OFF,ON or OFF:The power
supply has a fault. Replace the power supply.
OFF,OFF,OFF:There
is no power detected. Ensure that the power cable is connected at
the node and 2145 UPS-1U. If the AC LED does not light, check the
status of the 2145 UPS-1U to which the power supply is connected.
Follow MAP 5150 2145 UPS-1U if the UPS-1U is showing no power or an
error; otherwise, replace the power cable. If the AC LED still does
not light, replace the power supply.
OFF,OFF,ON:The power supply
has a fault. Replace the power supply.
OFF,ON,OFF:Ensure that
the power supply is installed correctly. If the DC LED does not light,
replace the power supply.
Possible Cause-FRUs or other:
Failed
PSU:
- Power supply (90%)
- Power cable assembly (5%)
- System board (5%)
Missing PSU:
- Power supply (19%)
- System board (1%)
- Other: Power supply not correctly installed (80%)