Before you install a
system, your physical environment must meet certain requirements. This includes verifying that adequate
space is available and that requirements for power and environmental
conditions are met.
Safety notices
Use the following general
safety information for all rack-mounted devices:
DANGER
Observe the following precautions when working
on or around your IT rack system:
- Heavy equipment–personal injury or equipment damage might result
if mishandled.
- Always lower the leveling pads on the rack cabinet.
- Always install stabilizer brackets on the rack cabinet.
- To avoid hazardous conditions due to uneven mechanical loading,
always install the heaviest devices in the bottom of the rack cabinet.
Always install servers and optional devices starting from the bottom
of the rack cabinet.
- Rack-mounted devices are not to be used as shelves or work spaces.
Do not place objects on top of rack-mounted devices.
- Each rack cabinet might have more than one power cord. Be sure
to disconnect all power cords in the rack cabinet when directed to
disconnect power during servicing.
- Connect all devices installed in a rack cabinet to power devices
installed in the same rack cabinet. Do not plug a power cord from
a device installed in one rack cabinet into a power device installed
in a different rack cabinet.
- An electrical outlet that is not correctly wired could place hazardous
voltage on the metal parts of the system or the devices that attach
to the system. It is the responsibility of the customer to ensure
that the outlet is correctly wired and grounded to prevent an electrical
shock. (R001 part 1 of 2)
CAUTION:
- Do not install a unit in a rack where the internal rack ambient
temperatures will exceed the manufacturer's recommended ambient temperature
for all your rack-mounted devices.
- Do not install a unit in a rack where the air flow is compromised.
Ensure that air flow is not blocked or reduced on any side, front,
or back of a unit used for air flow through the unit.
- Consideration should be given to the connection of the equipment
to the supply circuit so that overloading of the circuits does not
compromise the supply wiring or overcurrent protection. To provide
the correct power connection to a rack, refer to the rating labels
located on the equipment in the rack to determine the total power
requirement of the supply circuit.
- (For sliding drawers) Do not pull out or install any drawer or
feature if the rack stabilizer brackets are not attached to the rack.
Do not pull out more than one drawer at a time. The rack might become
unstable if you pull out more than one drawer at a time.
- (For fixed drawers) This drawer is a fixed drawer and must not
be moved for servicing unless specified by the manufacturer. Attempting
to move the drawer partially or completely out of the rack might cause
the rack to become unstable or cause the drawer to fall out of the
rack. (R001 part 2 of 2)
Important: In addition, remember the
following guidelines:
- The rack design must support the total weight of the installed
enclosures. Incorporate stabilizing features suitable to prevent the
rack from tipping or being pushed over during installation or normal
use.
- The rack design must consider the maximum enclosure operating
ambient temperature of 35-degrees C (95-degrees Fahrenheit).
- The rack must have a safe electrical distribution system. It must
provide overcurrent protection for the enclosure and must not be overloaded
by the total number of enclosures installed. Observer the electrical
power consumption rating that is shown on the nameplate.
- The electrical distribution system must provide a reliable ground
for each enclosure in the rack.
Power requirements for each power supply
To aid in power and cooling requirements planning, Table 1 lists the rating
of each power supply unit (PSU) by enclosure. Each enclosure contains
two AC PSUs for redundancy. The power rating values represent the
total power drawn by both PSUs. The power that is used by the system
depends on various factors, including the number of enclosures and
drives in the system and the ambient temperature.
Table 1. Power specifications per power supply
PSU |
Input power requirements |
Maximum input current |
Maximum power output |
Caloric value (BTU/hr) |
AC 800 W |
Single phase AC: 100 V to 127 V or 200 V
to 240 V Frequency: 50-60 Hz
|
100 V to 127 V 9 A 200 V to 240 V 4.5
A
|
800 W |
2730 |
The measurements that are shown in the following tables
were obtained in the specific operating environment and under the
conditions described. These measurements are presented as an illustration;
measurements that are obtained in other operating environments might
vary. Conduct your own testing to determine specific measurements
for your environment.
Table 2 shows
examples of the power ratings of Lenovo Storage V series systems with different drive configurations.
Table 2. Power rating examples for control enclosures.
Drive type |
Lenovo Storage V3700 V2 |
Lenovo
Storage V3700 V2 XP |
Lenovo Storage V5030 |
Average |
Peak |
Idle (Average) |
Average |
Peak |
Idle (Average) |
Average |
Peak |
Idle (Average) |
24-off Flash |
|
|
|
287 W |
292 W |
245 W |
|
|
|
24-off 15 K |
|
|
|
|
|
|
366 W |
370 W |
341 W |
24-off 10 K |
|
|
|
327 W |
327 W |
306 W |
|
|
|
12-off LFF NL |
252 W |
254 W |
242 W |
|
|
|
292 W |
|
277 W |
Workload: 70/30 random cache miss; worst of 4 K or 256 K block
size.
|
Table 3 shows
examples of the power ratings of Lenovo Storage V series expansion enclosures with different drive configurations.
Table 3. Power rating examples for expansion enclosures.
Drive type |
Expansion enclosure |
Average |
Peak |
Idle (Average) |
24-off 15 K |
234 W |
245 W |
199 W |
24-off SFF NL |
193 W |
|
|
12-off LFF Flash |
150 W - 180 W |
|
|
12-off LFF NL |
166 W |
|
165 W |
Workload: 70/30 random cache miss; 4 K block size.
|
Temperature requirements
Ensure that the
temperature and humidity in the environment falls within the ranges
shown in
Table 4. System
airflow is from the front to the rear of each enclosure:
- Airflow passes between drive carriers and through each enclosure.
- Airflow for the upper 4U of the 5U enclosure enters the front,
passes between the disk drives, and exits through the large fans in
the rear of the enclosure.
- Airflow for the lower 1U of the 5U enclosure is driven through
the power supplies via 40mm X 56mm fans. Air continues through the
chassis cooling the ESMs or controllers and exits the rear of the
enclosure.
- The combined power and cooling module exhausts air from the rear
of each canister.
Table 4. Temperature requirements
Environment |
Ambient temperature |
Altitude |
Relative humidity |
Maximum dew point |
Operating |
10° C to 35° C (50° F to 95°
F) |
0 - 3050 m (0 - 10,006 ft) |
20% to 80% non-condensing |
21°C (69° F) |
Non-operating |
-10° C to 50° C (14° F to 125°
F) |
0 - 3050 m (0 - 10,006 ft) |
8% to 80% non-condensing |
27°C (80° F) |
Storage |
1° C to 60° C (33° F to 140°
F) |
No limit |
5% to 80% non-condensing |
29°C (84° F) |
Shipping |
-40° C to 60° C (-40° F to 140°
F) |
No limit |
5% to 100% non-condensing |
29°C (84° F) |
Physical characteristics
Table 5 summarizes the
dimension and weight information for the Lenovo Storage V series control and expansion enclosures. Ensure that
the rack has enough available space to support each type of enclosure.
Table 5. Enclosure physical characteristics
Enclosure type |
Model |
Height |
Width |
Depth |
Maximum weight |
Drive ready (without drive modules) |
Fully configured (with drive modules) |
Control enclosures (12 LFF
drive slots) |
- Lenovo Storage V3700 V2 (2077-112 / 2078-112)
- Lenovo
Storage V3700 V2 XP (2077-212 / 2078-212)
- Lenovo Storage V5030 (2077-312 / 2078-312)
|
8.7 cm
(3.4 in)
|
48.3 cm
(19.0 in)
|
55.6 cm
(21.9 in)
|
18.0 kg
(39.6 lb)
|
28.3 kg
(62.2 lb)
|
Control enclosures (24 SFF
drive slots) |
- Lenovo Storage V3700 V2 (2077-124 / 2078-124)
- Lenovo
Storage V3700 V2 XP (2077-224 / 2078-224)
- Lenovo Storage V5030 (2077-324 / 2078-324)
|
8.7 cm
(3.4 in)
|
48.3 cm
(19.0 in)
|
55.6 cm
(21.9 in)
|
19.0 kg
(41.8 lb)
|
27.3 kg
(60.0 lb)
|
Expansion enclosure
(12 LFF drive slots) |
- Lenovo Storage V series (2077-12F / 2078-12F)
|
8.7 cm
(3.4 in)
|
48.3 cm
(19.0 in)
|
55.6 cm
(21.9 in)
|
16.4 kg
(36.1 lb)
|
26.7 kg
(58.9 lb)
|
Expansion enclosure
(24 SFF drive slots) |
- Lenovo Storage V series (2077-24F / 2078-24F)
|
8.7 cm
(3.4 in)
|
48.3 cm
(19.0 in)
|
55.6 cm
(21.9 in)
|
16.7 kg
(36.8 lb)
|
25.0 kg
(55.1 lb)
|
Enclosure clearances
Ensure that additional
clearance, as shown in Table 6, is available around each of the control and expansion enclosures.
Table 6. Enclosure clearances
Location |
Space requirement |
Reason |
Left and right sides |
50 mm (2 in.) |
Cooling air flow |
Back |
Minimum: 100 mm (4 in.). |
Cable exit |
Supported drives for enclosures
Table 7 shows the drive specifications
for the control and expansion enclosures of Lenovo Storage V series systems.
Table 7. Drive specifications
Enclosure type |
Drive type and storage capacity |
Enclosures with 12 drive slots
- Lenovo Storage V3700 V2
- Lenovo
Storage V3700 V2 XP
- Lenovo Storage V5030
- Lenovo Storage V series expansion enclosure
|
- 3.5-inch 15 K RPM HDD (300 GB, 600 GB)
- 3.5-inch 10 K RPM HDD (900 GB, 1.2 TB, 1.8 TB)
- 3.5-inch NL HDD (4 TB, 6 TB, 8 TB)
|
Enclosures with 24 drive slots
- Lenovo Storage V3700 V2
- Lenovo
Storage V3700 V2 XP
- Lenovo Storage V5030
- Lenovo Storage V series expansion enclosure
|
- 2.5-inch 15 K RPM HDD (300 GB, 600 GB)
- 2.5-inch 10 K RPM HDD (900 GB, 1.2 TB, 1.8 TB)
- 2.5-inch NL HDD (2 TB)
- 2.5-inch SSD (400 GB, 800 GB, 1.6 TB, 3.2 TB, 3.84 TB, 7.68 TB,
15.36 TB)
|
Shock and vibration specifications
Table 8 provides the shock testing results for each Lenovo Storage V series system.
Table 8. Shock testing specifications
Shock categories |
Test level |
Performance |
Operational |
5 g 10 ms 1/2 Sine |
<=25 g 10 ms |
Non-operational |
30 g 10 ms 1/2 Sine |
<=75 g 11 ms |
Table 9 provides the vibration testing results for Lenovo Storage V series systems.
Table 9. Vibration testing specifications
Vibration categories |
Test level |
Performance |
Operational |
0.21 grms 5-500 Hz Random |
Throughput loss <=10% FCAL <= 0.68 grms |
Non-operational |
1.04 grms 2-200 Hz Random |
<=3.12 grms |
Shipping |
0.3 g 2-200 Hz Sine |
<=5 g |
Rotational vibration |
Normal operation performance measurements
in enclosure with no external vibration. |
Throughput loss for all drives of the same type
within performance profile. |
Support rail specifications
Table 10 provides the supported depth of the rack for each Lenovo Storage V series system.
Table 10. Supported rack depth
Rack |
Supported depth |
Standard, 19-inch |
69.0 cm to 75.0 cm |