584: The 2145 UPS-1U is overloaded.

Explanation

A problem with output overload has been reported by the uninterruptible power supply 2145 UPS-1U. The Overload Indicator on the 2145 UPS-1U front panel is illuminated red.

User Response

  1. Ensure that only one 2145 is receiving power from the 2145 UPS-1U. Also ensure that no other devices are connected to the 2145 UPS-1U.
  2. Disconnect the 2145 from the 2145 UPS-1U. If the Overload Indicator is still illuminated, on the disconnected 2145 replace the 2145 UPS-1U.
  3. If the Overload Indicator is now off, and the node is a 2145-CG8 or 2145-CF8, on the disconnected 2145, with all outputs disconnected, determine whether it is one of the two power supplies or the power cable assembly that must be replaced. Plug just one power cable into the left hand power supply and start the node and see whether the error is reported. Then shut down the node and connect the other power cable into the left hand power supply and start the node and see whether the error is repeated. Then repeat the two tests for the right hand power supply. If the error is repeated for both cables on one power supply but not the other, replace the power supply that showed the error; otherwise, replace the power cable assembly.

Possible Cause-FRUs or other: