Explanation
The output load on the UPS exceeds the specifications, as reported by UPS alarm bits.
User Response
- Ensure that only appropriate systems are receiving power from the UPS. Also, ensure that no
other devices are connected to the UPS.
- Exchange, in the sequence shown, the FRUs for new FRUs. If the Overload Indicator is still
illuminated with all outputs disconnected, replace the UPS.
- Check node status. If all nodes show a status of "online", mark the error that you have
just repaired "fixed". If any nodes do not show a status of "online", go to start MAP. If
you return to this step, contact your support center to resolve the problem.
- Go to repair verification MAP.
Possible Cause-FRUs or other:
- Power cable assembly (50%)
- Power supply assembly (40%)
- UPS assembly (10%)