1135: UPS ambient temperature threshold exceeded

Explanation

The system UPS reported an ambient over temperature. The UPS switches to Bypass mode to cool down.

User Response

  1. Power off the nodes that are attached to the UPS.
  2. Turn off the UPS, and then unplug the UPS from the main power source.
  3. Ensure that the air vents of the UPS are not obstructed.
  4. Ensure that the air flow around the UPS is not restricted.
  5. Wait for at least five minutes, and then restart the UPS. If the problem remains, check the ambient temperature. Correct the problem. Otherwise, exchange the FRU for a new FRU.
  6. Check node status. If all nodes show a status of "online", mark the error that you have just repaired as "fixed". If any nodes do not show a status of "online", go to start MAP. If you return to this step, contact your support center to resolve the problem with the UPS.
  7. Go to repair verification MAP.

Possible Cause-FRUs or other:

2145 UPS electronics unit (50%)

Other:

The system ambient temperature is outside the specification (50%)