Explanation
The system internal temperature sensor has reported that the temperature warning threshold has
been exceeded.
User Response
- Ensure that the internal airflow of the node has not been obstructed.
- Check node status. If all nodes show a status of "online", mark the error that you have
just repaired "fixed". If any nodes do not show a status of "online", go to the start MAP.
If you return to this step, contact your support center to resolve the problem.
- Go to repair verification MAP.
For the 2145-DH8 and 2145-CF8 only:
- Check for external air flow blockages.
- Remove the top of the machine case and check for missing baffles,
damaged heatsinks, or internal blockages.
- If the problem persists after taking these measures, replace the
CPU assembly FRU if 2145-DH8 or 2145-CF8.
Possible Cause-FRUs or other:
2145-CF8 or 2145-CG8
- Fan module (20%)
- System board (5%)
- Canister (5%)
Possible Cause-FRUs or other:
Other:
Airflow blockage (70%)