Lenovo Storage V7000 enclosure location guidelines

Consult these guidelines when you plan the location of a control enclosure, and the expansion enclosures that are to be attached to it. A maximal configuration spans multiple racks, one of which contains the file modules. If multiple racks are required, locate the racks next to one another.

Plan for one of these installations:
  • Control enclosure only
  • Control enclosure plus one or more expansion enclosures
  • Expansion enclosure only
  • Another control enclosure plus one or more expansion enclosures

Each control enclosure contains two node canisters, forming an I/O group. The guidelines apply on an I/O group by I/O group basis.

Control enclosure only:

The control enclosure requires two standard rack units of space in a rack. If you plan to add expansion enclosures in the future, follow the guidelines for a control enclosure plus one or more expansion enclosures.

Control enclosure plus one or more expansion enclosures:

If you have one or more expansion enclosures, position the control enclosure in the center of the rack to make cabling easier. Balance the number of expansion enclosures above and below the control enclosure.

Lenovo Storage V7000 Gen2 requirements:
  • Each enclosure requires two standard rack units of space in a rack.
  • Attach no more than 10 expansion enclosures to port 1 of the control enclosure.
  • Attach no more than 10 expansion enclosures to port 2 of the control enclosure.
    Note: There is support for 10 expansions per chain, for a total of 21 enclosures to be included.
  • Position the enclosures together. Avoid adding other equipment between enclosures.
  • Position the enclosures in the rack so that you can easily view them and access them for servicing. This action also allows the rack to remain stable and allows two or more people to install and remove the enclosures.
Lenovo Storage V7000 Gen1 requirements:
  • Each enclosure requires two standard rack units of space in a rack.
  • Attach no more than five expansion enclosures to port 1 of the control enclosure.
  • Attach no more than four expansion enclosures to port 2 of the control enclosure.
  • Position the enclosures together. Avoid adding other equipment between enclosures.
  • Position the enclosures in the rack so that you can easily view them and access them for servicing. This action also allows the rack to remain stable and allows two or more people to install and remove the enclosures.
Expansion enclosure only:

Each enclosure requires two standard rack units of space in a rack. Identify the appropriate location for each enclosure by using the numbers on the front of the rack. When you add a single expansion enclosure to an existing network, it is preferable to add the enclosure directly below the control enclosure. When you add a second expansion enclosure, it is preferable to add the enclosure directly above the control enclosure. As more expansion enclosures are added, alternate adding them above and below the control enclosure.

Another control enclosure:

Put the second set of enclosures above or below the first set of enclosures. You can also add the second set of enclosures in a different rack.