80010901-0708ffff : Numeric sensor [NumericSensorElementName] going high (upper critical) has asserted. (Rear BP2 Temp)

Numeric sensor [NumericSensorElementName] going high (upper critical) has asserted. (Rear BP2 Temp)

This message is for the use case when an implementation has detected an Upper Critical sensor going high has asserted.

May also be shown as 800109010708ffff or 0x800109010708ffff

Severity

Error

Alert Category

Critical - Temperature

Serviceable

Yes

CIM Information

Prefix:PLAT

and ID:0494

SNMP Trap ID

0

Automatically Notify Support

No

User Response

  1. Make sure that the fans are operating, that there are no obstructions to the airflow (front and rear of the server), that the air baffle is in place and correctly installed, and that the server cover is installed and completely closed.
  2. Check the ambient temperature. You must be operating within the specifications (see Server Features and specifications for more information).
  3. Check fan cable on rear HDD cable is connected correctly.
  4. Check the fans on rear HDD cage are functional.
  5. Replace rear HDD drive cage.